Summary
I built a Home Assistant automation that force-charges the battery from the grid when Italy's Civil Protection department (DPC) issues a severe weather alert — similar to Tesla Powerwall's "Storm Watch" — so the battery is full before a possible grid outage.
While implementing this, I hit a reproducible communication error trying to use "Passive" mode, and want to share both the bug and the workaround in case it helps others.
Environment
The bug: CRC errors on specific number/select writes
Setting
select.inverter_storage_control_modetoPassiveworks reliably every time — no errors.However, writing values to these entities consistently fails:
number.inverter_passive_grid_powernumber.inverter_passive_maximum_battery_powernumber.inverter_passive_minimum_battery_powerselect.inverter_timed_control(e.g. setting it toCharge)Every attempt (single writes, isolated, several seconds apart, at different times of day) raised:
custom_components.solarman.pysolarman.umodbus.client.serial.redundancy_check.CRCError: CRC validation failed. File ".../solarman/pysolarman/umodbus/client/serial/redundancy_check.py", line 76, in validate_crc File ".../solarman/pysolarman/umodbus/client/serial/rtu.py", line 183, in parse_response_adu File ".../solarman/pysolarman/__init__.py", line 296, in _parse_adu_from_sol_response File ".../solarman/pysolarman/__init__.py", line 311, in get_response File ".../solarman/device.py", line 67, in execute File ".../solarman/entity.py", line 149, in write File ".../solarman/number.py", line 68, in async_set_native_value A single, isolated
number.set_valuecall reproduces it every time (not a burst/rate issue — I tested one write at a time with delays in between). The underlying pysolarman client appears to retry internally (~17 log lines per failed attempt) before surfacing the exception to HA. Meanwhile,select.select_optiononstorage_control_modenever failed once, across many tests over several hours.I don't have a packet capture, but happy to gather one (or test a patch) if it helps — this felt like it could be either a timing/serial issue between the Solarman logger and the inverter, or a quirk specific to how these particular registers are written vs. read.
The workaround that ended up working
Instead of
Passive+ direct power setpoints, I:select.inverter_storage_control_modebetweenSelf UseandTime of Use— nonumber.set_valuecalls at all.This has been 100% reliable in testing — confirmed with
sensor.inverter_battery_currentflipping positive (charging) immediately after switching toTime of Use, and cleanly reverting when switching back toSelf Use.Why I'm posting this
Happy to share the automation YAML for the storm-watch use case if useful for the wiki examples.